Is there anything that can be used as an alternative to a traditional grounding pole that is buried in the ground?

Is it possible to use a lightbulb, a series of lightbulbs, or maybe an inductor in place of the connection to earth and eliminate the voltage by converting into something harmless like light?

3 Answers3

3

No it’s not. The purpose of the ground connection is that in the event of a fault where a live wire contacts some exposed metal, the earth connection prevents a large voltage from presenting, and sufficient current flows to trip a breaker or fuse very quickly. If you put a light bulb in series then the bulb would illuminate to indicate a fault condition, but a user would still be exposed to mains voltage.

Frog
  • 7,287
  • 1
  • 9
  • 13
2

You could power the appliance through an isolating transformer.

that would prevent fault currents from seeking a path to ground.

1

The pole in the ground is not actually the most important part of the grounding system. The bond to "neutral" and the fact that "ground" is connected to all exposed metal is the most important part. The goal is to have all exposed conducting surfaces at the same electrical potential. Sticking a pole in the ground and connecting a ground wire to it just makes sure that that potential is the same as earth itself. But if someone came to my house and cut the wire to the pole in the ground, I might never know.

This is really a big and complex topic. Why are you asking? Maybe if you explain more of your thinking someone can provide you a better answer.

user57037
  • 29,324
  • 1
  • 30
  • 85
  • Is neutral bonded to earth at my house connection? – Indraneel Dec 05 '20 at 10:26
  • that's kind of hard to answer without more information. – Jasen Слава Україні Dec 05 '20 at 10:36
  • @Indraneel I have not visited your house. But, in the United States (which is where I live) the electrical code requires that neutral be bonded to "ground" in one and only one place in the home. Also, most generators have neutral bonded to "ground" inside the generator (there are exceptions too complicated to get into). Even if the generator is not actually tied to ground via a metal rod. – user57037 Dec 05 '20 at 18:49