Isolation transformers provide a 0 V between their hot wire and ground. After not understanding why that is, I doubted how earth grounding make a potential difference with me in first place.

First I know that there must some sort of a loop (that's basic) for the current to flow and second the must be a potential difference between two points in that loop.

Well in case you touched a grounded instruments and the live wire of the outlet, ground wire is already shorted with the neutral wire in the main panel so that's a loop. My question now is I don't see any kind of a loop when you for example touch a live wire with barefoot. (I mean the grounding rod is connected outside the house it's unlikely that the resistive path between me and it all the way there is allowing any current to flow.)

To sumup my Question ( May be it's to be considered two questions Actually )

  • Why Do I get shock When standing on a barefoot while touching a live wire When There's no return path ( at least the way I see it )

  • And How does isolation transformers prevent shocks when I touch a grounded instruments or with barefoots on the ground

enter image description here

Mahmoud Salah
  • 488
  • 4
  • 17
  • 1
    Your question is worded...strangely...I am not sure what you are trying to ask. Are you just asking how you can be connected to the ground rod outside the house when standing on the floor inside the house since there is no continuous copper connection between your feet and the ground rod? – DKNguyen Sep 03 '20 at 22:03
  • @DKNguyen Yup and how is that different when dealing with isolation transformers ( sorry for the confusion ) – Mahmoud Salah Sep 03 '20 at 22:07
  • 1
    Draw a diagram and add it to your question. – Transistor Sep 03 '20 at 22:07
  • 4
    The premise of your question is simply false. Isolation transforms do not provide zero voltage between their output and input, they provide extremely high impedance. Make one connection across the transfomer, and other points may now have a lethal voltage on them with the potential for meaningful current to flow. – Chris Stratton Sep 03 '20 at 22:39
  • Related: https://electronics.stackexchange.com/questions/519818/can-you-get-shocked-if-you-touch-a-hot-wire-whilst-perfectly-electrically-insula – P2000 Sep 04 '20 at 00:16
  • @ChrisStratton I took the graph and the Information from the "Practical Electronics for Inventors Book" And I am not sure What You are trying to say actually Do you refer to the Electrostatic potential that will be formed between the isolation transformer and the ground ? – Mahmoud Salah Sep 04 '20 at 13:59
  • 1
    The diagram is simply WRONG. Until you make some connection across the isolation transformer, the voltage across it (or between its outputs and ground) will be effectively indeterminate. Once you make one connection, the voltage of the other points will be fixed relative to that. The situation depicted in the diagram is self-conflicting, and impossible. – Chris Stratton Sep 04 '20 at 14:02

3 Answers3

3

Why Do I get shock When standing on a barefoot while touching a live wire When There's no return path

If there is no return path you will not be exposed. But there is a return path: the ground wiring in your home is tied to earth through a pad or rod, and to neutral at the panel. This means that the ground under your feet is electrically connected to the neutral wire leading back to the voltage source (e.g. your neighbourhood "step down" transformer)

See the picture below which shows that connection in the panel. (Ignore the subpanel/panel split, the point is that it shows the neutral bonded to the ground at the panel.)

enter image description here

And How does isolation transformers prevent shocks when I touch a grounded instruments or with barefoots on the ground

With an isolation transformer the live and neutral have an electrostatic potential w.r.t. earth, "floating" at possibly very high voltages. They can zap you, but likely won't kill. As long as the neutral or live is not earth grounded, no circuit forms when touched bare feet.

The diagram in your question incorrectly annotates the neutral to ground voltage as 0V. The "stabilization" shown (as 0V) requires a high-ohmic or low-ohmic grounding to neutralize the potential.

A high-ohmic earthing is used to stabilize the potential while avoiding a dangerous ground loop. A low-ohmic earthing is used to protect metal housings or exposed metal parts if a short from live to metal should occur, thus tripping a ground fault interrupter or a over-current breaker before a fire is started or a user is imperilled.

As drawn, there is no earthing, and that voltage to earth is an unknown.

Here is an example of an impedance grounding on the secondary side: (it's for a 3-phase system, but the principle is the same)

enter image description here

The high electrostatic potential on the isolated side would not be caused by the generator/transformer, but rather through other causes of charge accumulation.

Sometimes no path is required to feel a shock, e.g. when taking-in or relieving a charge between two bodies. This would be something like a capacitive in-rush zap. Kids experience this on a playground, when coming off the bottom of a plastic slide.

Whether the transformer or generator (the isolated source) requires earth grounding on the secondary side, depends on whether the consuming device is fully enclosed with the isolated source. If not, electrical codes often require low-ohmic earth grounding, and only a ground-fault interrupter will provide adequate protection, not the isolation.

Livestock electrical fences work on this principle: they provide a high voltage spike to overcome a (high resistive) path through earth.

enter image description here

(Image from https://www.stafix.com/en-us/helpful-information/grounding-your-energizer )

P2000
  • 3,167
  • 7
  • 23
  • But According to my understanding now that If The source or The neighboring transformer Wasn't grounded I will not get electrocuted when I touch a fault short live case for example since this grounding must be there in both sides So We can just eliminate the grounding all together from both sides and nothing will happen if I touch a live metal box... Right? – Mahmoud Salah Sep 04 '20 at 13:53
  • 1
    if the source is not grounded but you are, live & neutral will float. The ESD or any magnetic/capacitive coupled voltage to the metal casing / pipes etc... is then your hazard, and indeed not the current through the transformer. Ground the casing, and that hazard goes away, but now you have a possible high voltage between metal and live/nautral, causing arcing (fire) or injury. Ground metal and neutral, and all voltages are no more than 120/240 above earth. Then the current through ground is your enemy, and a GFI will protect you. – P2000 Sep 04 '20 at 14:50
2

The floor and soil don't have an overly low specific resistance, but it provides a lot of area for the current to flow through (as do your feet compared to the contact area of a wire). Combine this with the fact that wall voltages are high and not much current needs to flow to do some damage to your body.

So it follows that if the resistance between the transformer windings is much higher than the soil and earth, then it should be obvious how the isolation transformer protects you. It disconnects the ground potential on the primary from the 0V on the secondary and lets the 0V float so you must touch both secondary wires to get shocked. If you just touch one secondary wire, the potential at that wire becomes equal to your potential and the potential difference on the other terminal floats higher or lower maintaining the same voltage between secondary terminals.


You seem to be questioning how you could possibly be connected to the soil or the ground rod outside when you are several floors up in your building. Let's do some math.

For example, the resistance of rubber is on the order of \$10^{13}\$ Ohms-meters. This should be quite a bit higher than most materials. The resistance of copper is on the order of \$10^{-8}\$ Ohm-meters. So that's a difference of \$10^{11}\$ times. We would need an area of rubber \$10^{11}\$ larger than the area of the copper for it to be equally conductive.

The area for 16AWG wire running to your toaster is \$1.31mm^2\$. The area of your feet is about \$0.09m^2 = 8100mm^2\$ That's on the order of \$10^{3}\$ times more area. So your feet have a lot more area than the wire but but nowhere near \$10^{11}\$, right?

But let's try and guess the area of your entire floor or the cross section of your building. Let's just pick something small, say \$10m \times 10m\$ = \$100,000,000mm^{2}\$ That's \$10^{7}\$ times more area. Getting closer to \$10^{11}\$.

But now consider that you will get hurt by a lot less current than something like a toaster will. Just a few mA is enough. That 16AWG wire was sized to carry 15A to the toaster but you can be hurt by 5mA. That's a difference of current on the order of \$10^{3}\$. The 16AWG wire powering the toaster could be a thousand times higher in resistance and still hurt you.

So if we combine the ratio of \$10^{7}\$ and \$10^{3}\$ together, that gives you \$10^{10}\$ which is getting pretty close to the \$10^{11}\$ ratio. And remember, we used rubber which is a better insulator than most of the things the soil, floor, and building are made of. We also ignored the fact that there are grounded metal beams and pipes that let the charge take shortcuts up your building towards you.

**EDIT: Whoops, \$10^{13}\$ divided by \$10^{-8}\$ is \$10^{21}\$, not \$10^{11}\$. The biggest issue is probably that I should not have used rubber. I had trouble finding good conductivity numbers for dry wood or cured concrete. Wood varied from few gigaOhms when dry to hundreds of megaOhms with just a little bit of moisture content, to few kilOhms when damp. Resistivity of rock is surprisingly low, often much less than 10megaOhms, even when dry.

If you used a few hundred megaOhms, that would cut off about \$10^5\$ compared to using rubber so you would only need \$10^{16}\$ instead of \$10^{21}\$ more area.

enter image description here https://ieeexplore.ieee.org/document/6441387

enter image description here http://www.geonics.com/pdfs/technicalnotes/tn5.pdf

DKNguyen
  • 56,670
  • 5
  • 69
  • 160
  • I don't really see how the resistance from my body to the ground of my apartment 4 floors up the ground for instance far from the grounding rod have much less resistance than the transformers windings – Mahmoud Salah Sep 03 '20 at 22:19
  • 1
    @MahmoudSalah It's a bit unintuitive but you are probably not thinking about the area available for the current to travel through. Resistance over a long distance can be reduced by spreading it out over a huge area which the building has plenty of. – DKNguyen Sep 03 '20 at 22:21
  • So does this mean that the ground at the moment I am electrocuting is acting like a live wire will it light an LED for Example or the distribution over a long area will make sure that doesn't happen + If it's so dangerous why grounding in the first place If we can just keep them all floating ? – Mahmoud Salah Sep 03 '20 at 22:23
  • One more thing Some countries Doesn't have a grounding rods or third connection in the first place but there is still shockes from live wires Like in My country – Mahmoud Salah Sep 03 '20 at 22:25
  • 1
    @MahmoudSalah See edit. I forget the reason why you don't keep everything floating but I think it has to do with predictability. If you don't ground it, there is nothing stopping the both terminals from floating so high above ground that sparks literally jump out at you from the socket. I think it has to do with wide area of the power grid being able to collect charge over a vast area. – DKNguyen Sep 03 '20 at 22:46
  • 2
    @MahmoudSalah The third connection is actually there to PREVENT shocks (when used properly). It connects to the case so that if a live wire gets loose inside and touches the case it shorts to ground. If it were not there, the case would be live and when you touched it, the current would go to ground through you. From the math example above, you can see that you don't actually need ground rods to increase the conductivity from the earth to your feet. Just a bunch of area of other material is enough. – DKNguyen Sep 03 '20 at 22:59
  • But If there's no grounding system at all when I touch this case ( The way I get it ) I will not be electrocuted since the source isn't grounded either ( except from the ESD between bodies for instance ) – Mahmoud Salah Sep 04 '20 at 13:55
  • @MahmoudSalah The source is grounded somewhere, even if it is just at the power plant. Just because it has not been made accessible to you doesn't mean it's not there. – DKNguyen Sep 04 '20 at 13:57
  • Right But I am imagining if it weren't grounding at all my understanding will be right ? if there's no grounding i will not get zapped since there's no compensation of this lacked electrons through my body or something – Mahmoud Salah Sep 04 '20 at 14:01
  • And If I tried to connect a Battery for Example and grounded The load terminal and The negative terminal Without any other return path Would It close The circuit ? – Mahmoud Salah Sep 04 '20 at 14:02
  • 2
    @MahmoudSalah If you're not grounded at all (say floating in the air) you would be a lot safer. A battery is too low voltage to push through everything. But if you had a 200V or 400V battery, I would not try stabbing one terminal into the floor through a large metal plate and touching the other contact with your finger. I don't recommend touching it at all because you don't know if there is some residue that has leakage currents. – DKNguyen Sep 04 '20 at 14:04
1

One of the misconceptions you are struggling with is earth resistance, you seem to think that earth resistance increases with distance. In reality earth resistance is a constant, if you can measure 1 ohm resistance between two electrodes a metre apart, you will also measure 1ohm between two electrodes 100m apart or 10km apart. What happens is that there are more current paths between points further apart; For electrodes 100m apart, the current paths can go 100m deep and 100m to the side, while resistance does vary with length, the relationship is resistance = length * area/volume , so if length , width and depth all vary together, the resistance is constant. The measured value of earth resistance is determined by the size of your earthing stake :- bigger stake = lower resistance. for lightning protection of large buildings they will often bury a metallic grid in the soil before the start of building.

In a building , there are earthing straps and metal plumbing and a metal building frame that join all the ground potential points together , if all exposed metal parts are connected together, they are the same potential during a fault or a lightning strike.

BobT
  • 624
  • 3
  • 8
  • "earth resistance is a constant", I vaguely recall this from classes years ago. Can you point to a physics/ee text for the math behind this? A quick search didn't bring up anything as succinctly as you put it. Will be a good refresher. – P2000 Sep 03 '20 at 23:40
  • This has nothing to do with the questions which were asked, which are not about current paths through soil. – Chris Stratton Sep 04 '20 at 02:17
  • @ChrisStratton I think it is pretty relevant. – DKNguyen Sep 04 '20 at 13:58
  • Then you really didn't understand the question. – Chris Stratton Sep 04 '20 at 14:06
  • @ChrisStratton The OP did say " (I mean the grounding rod is connected outside the house it's unlikely that the resistive path between me and it all the way there is allowing any current to flow.)" which indicates a lack of knowledge of how earthing systems work, I was just supplying some supplemental information, that would better allow him to understand parts of the puzzle. Poorly phrased questions don't have unique, correct or unambiguous answers. Add your own answer if you have a better one. – BobT Sep 04 '20 at 22:15
  • @P2000 I did a google search and couldn't find any elegant reference to it. In my prior job we looked at measuring em signal propagation in coke (the stuff used in ironmaking) we had a skip full of it and we hammered rods in various places, and did indeed find the resistance was constant, Decades later we did some geophysical studies of magneto-tellurics, and also found the same thing with soil – BobT Sep 04 '20 at 22:37
  • Well on "physics" I found something. I though it should be close to the problem of finding the resistance between any two points on a grid of 1Ohm resistors. For 2D the answer is a constant! 4/pi-1/2 = 0.77 Ohm and that rang a bell. 3D along the edge surface of a solid may be different, but I wouldn't be surprised if it's a constant too. Thanks for the prompt, Bob https://physics.stackexchange.com/questions/2072/on-this-infinite-grid-of-resistors-whats-the-equivalent-resistance – P2000 Sep 04 '20 at 23:29
  • @P2000 I think it is related to how the surface area to volume ratio has the units of m^-1 , and resistivity is in ohm-m , using resistivity you would think that further apart is higher resistance , but the two points are simply points on two spherical shells so as you go further apart the SAV drops , so the ohm-metre and metre^1 cancel out. and you are left with just ohms. – BobT Sep 05 '20 at 01:45
  • @BobT - connection between where the OP stands and the ground rod is not through the soil. – Chris Stratton Sep 05 '20 at 01:59
  • @Chris , the OP says "And How does isolation transformers prevent shocks when I touch a grounded instruments or with barefoots on the ground" It's a bit ambiguous whether he is (a) standing barefoot on something that is connected ohmically to a ground potential, or (b) is actually standing on dirt, soil, earth. loam , terra-firma, regolith etc – BobT Sep 05 '20 at 08:21
  • @BobT the question is about ground as a circuit node, not the actual soil. Look way up at the diagram in the question, which presents a situation which is simply impossible - that is the root of the issue. It's not about soil at all. – Chris Stratton Sep 05 '20 at 21:36